Quote:
A 15A circuit on a 120V system can in theory provide 1800W of power to a connected device, but in reality a 15A breaker is designed to trip before it reaches that level - probably before 1500W (12.5A)
Sorry Gonk but I just can't agree with that statement. If anything the breaker will trip at a slightly higher level. Since breakers are designed and rated at a temp of 40C (104F) and usually are not in an environment of such high temps, the tripping amperage would be slightly higher. According to a typical manufacturers Trip Chart a breaker will carry the full current rating indefinitely and will carry additional current for proportionally less time. The chart shows how a typical 15 amp breaker will carry 2 times the rated current (30 amps or 3600 watts) for 10 seconds and even carry 5 times the rated current (75 amps or 9000 watts) for 1 second.